 Post subject: Arc Flash Studies Are POINTLESS - Change My Mind
PostPosted: Tue Oct 20, 2026 11:57 am 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 23
The utility fault contribution can change at any time without any notice. A label printed today could be useless tomorrow and we wouldn't know


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Studies Are POINTLESS - Change My Mind
PostPosted: Tue Oct 20, 2026 2:09 pm 
Arc Level

Joined: Mon Jan 18, 2010 11:35 am
Posts: 617
Location: Wisconsin
Most companies will know when they have lost their utility power.

A transformer change at a utility substation will not really affect the fault current at a customer purchasing power at secondary voltages like 480Y/277.
Most customers will experience their 'worst' arc flash values when they are on generator power. Less available fault current means protective devices do not enter the Instantaneous range.

We ran multiple scenarios for arc flash and typically reported the highest incident energy results regardless which scenario caused it..
At the least we ran infinite bus utility, normal reported fault current with all motors on, normal fault current with all motors off, and generator power.
Once data has been entered into a software package running multiple scenarios is not a large expense. I think my record was 15 scenarios.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883