 Post subject: Overduty Equipment
PostPosted: Thu Apr 09, 2026 6:22 am 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 16
I usually run my short circuit study using the ANSI standards and there are several over duty devices (about 20 devices). For arc flash, I run comprehensive method which results in only about 3 devices reported as over duty.

Would you only print the 3 over duty labels in comprenhsive or for this case would you run ansi arc flash? All equipment is 480 and 208V


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Overduty Equipment
PostPosted: Thu Apr 09, 2026 6:25 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 173
CB ratings are based on the ANSI standards...

Mike

PS Usually, the comprehensive and ANSI methods are pretty close. What is the margin of difference and can you give an example from your study of an overdutied device?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Overduty Equipment
PostPosted: Thu Apr 09, 2026 7:30 am 

Joined: Thu Dec 18, 2025 3:21 pm
Posts: 16
Hmm, you are correct. It was a user error, apparently there were some errors when I ran the SC eval and comprehensive wasn't updating. They are both showing the same now, thanks for the response. I would delete this post if I knew how LOL


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883