 Post subject: Why do Shallow enclosures produce a lower Incident Energy?
PostPosted: Wed Jan 04, 2023 4:54 am 

Joined: Tue May 22, 2012 12:08 am
Posts: 30
In results calculated using IEEE 1584-2018 equations, I have noticed that Incident Energy values are lower for Shallow enclosures than for Typical enclosures (when all parameters except Enclosure Depth are identical). See the attached image for some examples.

Attachment:
File comment: Screenshot of effect of Enclosure Depth on calculated Incident Energy
EnclosureDepthEffect.png
EnclosureDepthEffect.png [ 48.55 KiB | Viewed 83443 times ]


In past topics on this forum, members have commented that calculated Incident Energy will be lower for Shallow enclosures (see 2018 IEEE 1584 - Arc Flash and Shallow Enclosures and Implementing New 1584). Having looked closely at the Intermediate Incident Energy equation (Eq. 6), I can see why a lower energy value is generated.

What I would like to understand is why a shallower enclosure would in practice produce a lower Incident Energy. My simplistic understanding was that the larger the enclosure the more volume is available for the arc to disperse (and the effect of the arc would therefore be lessened) and conversely the smaller the enclosure the more focused the effects of the arc would be.

If anyone can shed any light, I would be very grateful.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Why do Shallow enclosures produce a lower Incident Energ
PostPosted: Wed Jan 04, 2023 6:41 am 

Joined: Tue May 22, 2012 12:08 am
Posts: 30
I've also just read a statement in IEEE Std 1584-2018 Annex G (G.9.4) which that states that Incident Energy test results were higher for enclosures with depth <= 203.2 mm (8 in) than those of depth > 228.6 mm (9 in). Is that a typo?

Here's a screenshot of the aforementioned excerpt...
Attachment:
File comment: Annex G.9.4 of IEEE Std 1584-2018
AnnexG_9_4.png
AnnexG_9_4.png [ 98.62 KiB | Viewed 83438 times ]


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Why do Shallow enclosures produce a lower Incident Energ
PostPosted: Sun Jan 08, 2023 4:19 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
w5m wrote:
In results calculated using IEEE 1584-2018 equations, I have noticed that Incident Energy values are lower for Shallow enclosures than for Typical enclosures (when all parameters except Enclosure Depth are identical). See the attached image for some examples.

Attachment:
EnclosureDepthEffect.png


In past topics on this forum, members have commented that calculated Incident Energy will be lower for Shallow enclosures (see 2018 IEEE 1584 - Arc Flash and Shallow Enclosures and Implementing New 1584). Having looked closely at the Intermediate Incident Energy equation (Eq. 6), I can see why a lower energy value is generated.

What I would like to understand is why a shallower enclosure would in practice produce a lower Incident Energy. My simplistic understanding was that the larger the enclosure the more volume is available for the arc to disperse (and the effect of the arc would therefore be lessened) and conversely the smaller the enclosure the more focused the effects of the arc would be.

If anyone can shed any light, I would be very grateful.


It is more about the focusing effect of the sides. If it is a shallow enclosure, the bus would be much closer to the opening and therefore not as much focus from the sides. Great question.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Why do Shallow enclosures produce a lower Incident Energ
PostPosted: Sun Jan 08, 2023 4:21 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1738
Location: Scottsdale, Arizona
w5m wrote:
I've also just read a statement in IEEE Std 1584-2018 Annex G (G.9.4) which that states that Incident Energy test results were higher for enclosures with depth <= 203.2 mm (8 in) than those of depth > 228.6 mm (9 in). Is that a typo?

Here's a screenshot of the aforementioned excerpt...
Attachment:
AnnexG_9_4.png


Hum.... (official response :lol:)

I'm going to need to look into that one.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Why do Shallow enclosures produce a lower Incident Energ
PostPosted: Wed Jan 11, 2023 2:41 am 

Joined: Tue May 22, 2012 12:08 am
Posts: 30
Happy New Year Jim and many thanks for your responses.

I hadn't considered that the sides would have less of a focusing effect in a shallow enclosure. That makes good sense.

Thanks for looking into the G.9.4 statement.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883