Author:  Tboy01 [ Wed Mar 01, 2023 9:51 am ]
Post subject:  Under calibrated PPE?

Hello everyone,

I am new to the forum.
I would like to ask ,in what way is 25 cal/cm2 arc protected clothing possible to be classified 2.cat.

Thanks for your help
Tibor

Author:  mayanees [ Mon Mar 06, 2023 10:51 am ]
Post subject:  Re: Under calibrated PPE?

70E Table 130.7(C)15(c) Personal Protective Equipment is the table used for the PPE Categories method. In that Table PPE 1 goes to 4 cals, PPE 2 goes to 8 cals, PPE 3 - 25 cals and PPE 4 - 40 cals.
Category 2 is good for 8 calories, but anything larger can be used for a lower incident energy rating, so a 25-cal PPE can be used for Cat 2.

Author:  Tboy01 [ Mon Mar 06, 2023 12:39 pm ]
Post subject:  Re: Under calibrated PPE?

mayanees wrote:
70E Table 130.7(C)15(c) Personal Protective Equipment is the table used for the PPE Categories method. In that Table PPE 1 goes to 4 cals, PPE 2 goes to 8 cals, PPE 3 - 25 cals and PPE 4 - 40 cals.
Category 2 is good for 8 calories, but anything larger can be used for a lower incident energy rating, so a 25-cal PPE can be used for Cat 2.


Thank you for your reply,
So, a cloth is marked with 25 cal/cm and 2 CAT.
Which one is relevant?

Author:  Tboy01 [ Thu Mar 09, 2023 12:58 am ]
Post subject:  Re: Under calibrated PPE?

mpparent wrote:
Might be helpful to take a picture of the tag and post it here.

Mike


Attachments:
File comment: There is an explanation
Képernyőkép 2023-03-09 085347.jpg
Képernyőkép 2023-03-09 085347.jpg [ 166.36 KiB | Viewed 37039 times ]

Author:  Tboy01 [ Fri Mar 10, 2023 12:45 am ]
Post subject:  Re: Under calibrated PPE?

mpparent wrote:
Does the garment have a tag on the inside, indicating its ATPV?

Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70

Author:  MarkusK [ Fri Mar 10, 2023 1:15 am ]
Post subject:  Re: Under calibrated PPE?

Tboy01 wrote:
mpparent wrote:
Does the garment have a tag on the inside, indicating its ATPV?

Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70


The class 2 refers to APC 2 (Arc Protection Class 2) according to IEC61482-1-2 (european Box Test) and is independent from the ATPV value

Author:  Tboy01 [ Fri Mar 10, 2023 2:33 am ]
Post subject:  Re: Under calibrated PPE?

MarkusK wrote:
Tboy01 wrote:
mpparent wrote:
Does the garment have a tag on the inside, indicating its ATPV?

Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70


The class 2 refers to APC 2 (Arc Protection Class 2) according to IEC61482-1-2 (european Box Test) and is independent from the ATPV value


Yes, it's clear.
I needed confirmation that I did indeed need to replace the protective clothing.
Thank you for the time you have spent on this topic

Sincerely
Tibor