 Post subject: 2018 NFPA 70E Changes Article
PostPosted: Sun May 21, 2017 2:14 pm
Offline
The 2018 Edition of NFPA 70E is quickly approaching. Here is an article of mine that was recently published in the May Edition of Electrical Contractor Magazine. As usual, some changes were minor, others were quite major. There is also quite a bit of reorganization.
Best Wishes,
Jim Phillips
jphillips@brainfiller.com
Report this post
 Post subject: Re: 2018 NFPA 70E Changes Article
PostPosted: Mon May 29, 2017 8:21 am
Offline
What's New? What's Changed? 2018 NFPA 70E Update wrote:
Boundary, Arc Flash: The revised definition [..] no longer uses the term "second degree burn" but instead "at which incident energy equals 1.2 cal/cm2." The revised informational note references the Stoll skin burn injury model.
NFPA 70E year 2004 assumed that the incident energy requirement increases below one second. A quote from NFPA 70E year 2004 "For situations where fault-clearing time is 0.1 second (or faster), the Flash Protection Boundary is the distance at which the incident energy level equals 6.24 J/cm^2 (1.5 cal/cm^2)." This reference was removed in NFPA 70E year 2012 edition. NFPA 70E year 2012 stated that "a second degree burn is possible by an exposure of unprotected skin to an electric arc flash above the incident energy level of 1.2 cal/cm2 ( 5.0 J/cm2 )" and assumes 1.2 cal/cm2 as a threshold incident energy level for a second degree burn for systems 50 Volts and greater. NFPA 70E year 2015 explicitly prohibited using incident energy and PPE category together. The NFPA Handbook from 2015 showed a sample label with fields to be filled in for "available incident energy" and "level of PPE" while just half a page earlier states that "available incident energy" cannot be included with the "PPE category" in table 130.7(c)15(A)(b).
The revised definition of arc flash boundary in NFPA 70E year 2018 is even more misleading. It also contradicts the accompanying revised informational note referencing the Stoll skin burn injury model. A quote from A.Stoll "Heat Transfer in Biotechnology" summarizes the issue of using a critical thermal load approach in determining arc flash boundary. The quote reads:
"Serious misconceptions have crept into this field of research through adoption of rule-of-thumb terminology which has lost its identity as such and become accepted as fact. A glaring example of this process is the “critical thermal load.” This quantity is defined as the total energy delivered in any given exposure required to produce some given endpoint such as a blister. Mathematically it is the product of the flux and exposure time for a shaped pulse. Implicit in this treatment is the assumption that thermal injury is a function of dosage as in ionizing radiation, so that the process obeys the "law of reciprocity," i.e., that equal injury is produced by equal doses. On the contrary, a very large amount of energy delivered over a greatly extended time produces no injury at all while the same "dose" delivered instantaneously may totally destroy the skin. Conversely, measurements of doses which produce the same damage over even a narrow range of intensities of radiation show that the "law of reciprocity" fails, for the doses are not equal."
I would strognly encourage the NFPA 70E committee members to consult ASTM F1959/F1959M Standard Test Method for Determining the Arc Rating of Materials for Clothing and see what is says about skin burn injury determination. For anyone else who doesn't have a copy of ASTM F1969, the standard reads:
"12.1.4 Predicted Second-Degree Skin Burn Injury Determination (Stoll Curve Comparison) — The time dependent averaged heat energy response for each panel [..] is compared to the Stoll Curve empirical human predicted second-degree skin burn injury model:
Stoll Response, cal/cm2 = 1.1991 * ti^0.2901
where ti is the time value in seconds of the heat energy determination and elapsed time since the initiation of the arc exposure. A second-degree skin burn injury is predicted if either panel sensor heat energy response exceeds the Stoll Response value (at time ti)."
Incident energy alone has no impact on thermal damage and blast pressure. One can expose himself to any arbitrary incident energy and suffer no damage as long as the energy is delivered at slow enough rate. On the other hand, an exposure to only a fraction of 1.2 cal/cm2 may result in incurable burn provided that the energy has been delivered fast enough. Read Evaluation of onset to second degree burn energy in arc flash hazard analysis or this forum thread at https://www.arcflashforum.com/viewtopic.php?f=34&t=2221 for more information. The issue of using incident energy as a measure of damage alone and without regard to the rate of the energy release has been raised to NFPA 70E committee before year 2015 edition was published but unfortunately the group failed to address the matter back in 2015. It seems the new upcoming NFPA 70E is to obscure the matter even more instead of admitting the glaring mistake and fixing it.
Michael Furtak, C.E.T.
http://arcadvisor.com
Report this post
PostPosted: Fri Jun 02, 2017 9:54 pm
Offline
IEEE 1584 is a theoretical only model. Really all the arc flash models are. It's pretty easy to poke huge gaping holes in them. But the model as it stands has withstood years of practical "tests". No need to switch from energy to flux unless it can be shown with direct evidence that it exceeds the 1584 track record.
Report this post
PostPosted: Sun Jun 04, 2017 11:31 am
Offline
Just to be clear, I've never mentioned IEEE 1584 in my post and I've never intended to "poke huge gaping holes" or critise the IEEE theoretical model in any way. Actually, the IEEE model provides for solving IEEE P1584 equations (5.8) and (5.9) based other than 1.2 cal/cm2 threshold incident energy technically allowing to use variable threshold incident energy to 2nd degree as a function of heat flux.
Of course, NFPA 70E is free to hold to its erroneous claim that the 1.2 cal/cm2 is the threshold incident energy level for a 2nd degree burn on a bare skin but the new NFPA 70E reference to Stoll model is appauling and misleading as A.Stoll had personally bewared of using the critical thermal load when determining arc flash boundary as cited above.
I also believe that the ASTM F1959/F1959M has been developed way prior to NFPA 70E adaptation of arc flash hazards. Hence it seems that NFPA 70E has switched from flux to energy, and not the other way around.