I’m working on a fault current calculation for a meter stack and had a question regarding series ratings.

According to the manufacturer, the Siemens QPH breaker can be series-rated with a Siemens 3VA6-H breaker, resulting in a load center feeder breaker with a 100kA AIC rating. Additionally, a Siemens QP breaker can be series-rated with a QPH breaker at 22kA.

My question is: if the feeder breaker (QPH) is part of a series combination rated at 100kA with the upstream 3VA6, can the downstream branch breakers (QP) also be considered as having a 100kA series rating? Or are they still limited to their own tested series rating (22kA with QPH)?

Attachments:
Screenshot 2026-04-02 110739.png
Screenshot 2026-04-02 110739.png [ 20.04 KiB | Viewed 1538 times ]

Author:  mpparent [ Thu Apr 02, 2026 8:51 am ]
Post subject:  Re: Meter Center Series Ratings

You would have to look in Siemens tables to see if the breakers "stack". However, I doubt it...best to double check.

Mike

Author:  bbaumer [ Fri Apr 03, 2026 4:07 am ]
Post subject:  Re: Meter Center Series Ratings

75kA available looks pretty high but not enough info to really evaluate. Are you confident in that value?

Also what Mike said RE: series ratings. Eaton has some info on tenant rating like what you have there with 3 breakers but the answer is what Mike said. You might be ok if the QP also has a rating with the 3VA6 but you'll need to look it up.

From Eaton. Siemens may be different:

Attachment:
Screenshot_20260403_071041_Chrome.jpg
Screenshot_20260403_071041_Chrome.jpg [ 712.14 KiB | Viewed 1469 times ]