It is currently Mon Jun 26, 2017 11:59 am
ekstra   ara
 Post subject: Distribution Feeder Arc Flash Calculation
PostPosted: Fri May 12, 2017 1:10 pm
Offline
OSHA States as a note in 1910.269 the following:
Note 2 to paragraph (l)(8)(ii): This paragraph does not require the employer to estimate the incident heat energy exposure for every job task performed by each employee. The employer may make broad estimates that cover multiple system areas provided the employer uses reasonable assumptions about the energy-exposure distribution throughout the system and provided the estimates represent the maximum employee exposure for those areas. For example, the employer could estimate the heat energy just outside a substation feeding a radial distribution system and use that estimate for all jobs performed on that radial system
It seems to me like you would have a higher incident energy further away from the substation because the further you go out the less fault current there is and therefore a longer trip time / arcing time. All the studies I have done have shown that to be true. It seems very odd that OSHA posted that note to me. Thoughts?
 Post subject: Re: Distribution Feeder Arc Flash Calculation
PostPosted: Sun May 14, 2017 9:46 am
Offline
I do not know OSHA's reasoning on that as studies I have done show that the incident energy can be higher the farther you get from the substation protective device. So I will look at some of the feeders to determine the IE on the farthest point from the sub protective device.
PostPosted: Mon May 15, 2017 9:49 am
Offline
Yes, you are correct, the arc flash energy can be higher the farther away you are from he substation. For fuse protected circuits, I would say that this is true. However, using relays, you may be able to set it so that the tripping time would be constant over the entire length of the feeder.
You can do this by using a 50 Element with a delay of 0.5 to 0.2 seconds. This is similar to the Short Time function of a low voltage circuit breaker. The pick up should be set 1.1 X times the minimum arcing (not bolted) fault current of the entire line.
PostPosted: Mon May 15, 2017 10:44 am
Offline
Also more modern relays have a Hot Line Tag feature which can be used to reduce the incident energy values also
PostPosted: Mon May 15, 2017 7:13 pm
Offline
In a constant time region as impedance increases (such as with longer cables), incident energy decreases as expected. Constant trip times for instance would be "insrantaneous" (51) regions,or at the two second cutoff.
In an inverse time region depending settings it can go up, down, or stay the same. In practice most of the time ".
Who is online
Users browsing this forum: No registered users and 1 guest
© 2017 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883