| Author: | bbaumer [ Sat Jun 27, 2026 8:22 am ] |
| Post subject: | Re: Unreasonable current during study |
Couple of questions: Are you using the same Data Block to display the results of the short circuit study results and the AF study results? Can you post a screen shot of your "reasonable" short circuit study results for comparison to the "unreasonable" results? Are you using the same short circuit calculation method for both the short circuit study and the AF study? What attribute in the Data Block is Isc 3P? Isc 3P is not an SKM default/base attribute name so whatever attribute it is has been renamed to Isc 3P. It is possible something has been edited incorrectly in the attribute in addition to the renaming. |
|
| Author: | Win Engineer [ Fri Jul 10, 2026 9:11 am ] |
| Post subject: | Re: Unreasonable current during study |
Use the Branch fault Current data block and see what fault current you have flowing through the system. I had a model years ago that was yielding some ridiculous fault currents on a 208V system and discovered that a bunch of 10HP motors had been entered at 10,000HP. You can imagine at 208V the fault contribution from the motors! That data block showed me the fault current coming back into the bus was really high and pointed me straight to the issue. |
|