MIControl wrote:
I have noticed that there are 2 different thought process expressed here regarding the HRC and associated levels of protection. I assume this is all in how you interpret the information in Table 130.7(C)(16).
Level 2 Arc-Rated Clothing, Minimum Arc Rating of 8 cal/cm2
Level 3 Arc-Rated Clothing Selected so That the System Arc Rating Meets the Required Minimum Arc Rating of 25 cal/cm2
Does this mean HRC 2 is only up to and including IE of 8 cal/cm2 and HRC level 3 is 8.1 cal/cm2 up to 25 cal/cm2?
Yes-This assumption is correct
Quote:
Annex H, Table H.2 states all HRC 1 & 2 together with clothing and gear rated for a minimum of 8 cal/cm2.
This appears to be a situation where we can read into this as far as we choose to, or not to for that matter.
Does anyone have any specific experience with this and can shed some light on this subject?
Annex H was installed as "Informative" guidance to help the reader understand requirements in 70E by providing examples or situations that may help in everyday situations in this case. The Annex refers basically to place qualified electrical workers in Cat 2 PPE for applicable tasks in the tabels. Note-this PPE may need to be changed or added to for other tasks that are associated with HRC 2 tasks. Read the note below the table to ensure you are compliant with the situation.