bbaumer wrote:
Yes. I have almost this exact situation on a current project, except the POCO gave me even less information so I have to run with what they are willing to provide. I know the primary voltage and the pad mount nameplate but they won't provide the primary fault current data. Only secondary 3 phase data. No SLG or X/R data. See below.
NOTE: THIS IS NOT ADVICE OR A GUARANTEED TO BE ACCURATE OR APPROPRIATE WAY OF HANDLING A SITUATION LIKE THIS. IT IS ONLY ONE EXAMPLE OF HOW I AM CHOOSING TO HANDLE IT IN ONE PARTICULAR INSTANCE.
Attachment:
combined poco xfmr skm.jpg
Very interesting! I never receive X/R data from the utility. It's also interesting that they're giving you info from the load side of the utility transformer...the local utilities I deal with tend to give fault information at the meters, which are always on or near the main service gear, and 25'-300' from the utility transformer. They also give service conductors, which since we can usually see where they terminate on the service equipment, is not always correct.
I see that you mention using 8.0 as a default X/R. Is that a generic default number you're pulling from somewhere, or something based on a standard you see from Utilities you deal with?