 Post subject: Fuses in parallel
PostPosted: Sun Jan 22, 2012 5:21 pm 

Joined: Sun Jul 22, 2007 5:00 pm
Posts: 36
Location: Stratham, SW Australia
When an arcing fault occurs downstream from two 100A fuses in parallel, can the fuses modelled by a single 100A fuse by shifting the current axis to the right by a factor of two to represent the time-current curve for the two parallel 100A fuses ?
The above assumes that the current divides equally between the two 100A parallel fuses.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Tue Jan 24, 2012 5:12 am 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1736
Location: Scottsdale, Arizona
mnewman wrote:
When an arcing fault occurs downstream from two 100A fuses in parallel, can the fuses modelled by a single 100A fuse by shifting the current axis to the right by a factor of two to represent the time-current curve for the two parallel 100A fuses ?
The above assumes that the current divides equally between the two 100A parallel fuses.


What voltage? Medium Voltage fuses have a parallel mounting for larger ratings. i.e. 540E which is made up of 2 - 300E fuses in parallel. 540E = (2 x 300E) x 90% The curve is specific for a 540. I did not overlay a shifted 300E TCC with a 540E but it looks like the shapes are similar.

In the U.S. we don't parallel LV fuses (except perhaps cable limiters on networks)

_________________
Jim Phillips, P.E.
Brainfiller.com


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Sat Jan 28, 2012 5:51 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
There is a small problem with this. The average fuse rating doubles but the fuse accuracy goes down. Fuse curves show a range of values to accomodate a +/-% factor. If you parallel them, you might get a batch which are both on the extreme to either the positive (bad from an arc flash point of view) or negative side.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fuses in parallel
PostPosted: Thu Dec 14, 2023 2:37 pm 

Joined: Thu Dec 14, 2023 2:29 pm
Posts: 3
I know this was post was made a long time ago, but maybe someone can still respond. so Jim Phillips gave the example of two fuses in parallel. But I have a situation where I have a medium voltage switchgear with 3 fuses in parallel with a total amperage of 1080A between the three. What would be the calculation for that; what would each fuse size be? Thank you


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fuses in parallel
PostPosted: Thu Dec 14, 2023 3:50 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 487
Location: Indiana
Here's another thread on this subject, low voltage version. It was never resolved though. Like a lot of posts on here, people try to help and answer the question but the OP disappears with no follow-up.

viewtopic.php?f=23&t=5609

You can model multiple fuses in parallel in SKM. Not sure about other programs. Never tried in etap and I don't have EasyPower.

That said, RE: your question, what are you trying to calculate or are you only trying to select fuses?

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fuses in parallel
PostPosted: Fri Dec 15, 2023 6:02 am 

Joined: Thu Dec 14, 2023 2:29 pm
Posts: 3
I am trying to calculate the fuse size. I have never seen a triple barrel per phase before. They want 1080A between the three fuses per phase, but I cannot determine what the E-rated fuse would be. I want to know if there is a calculation behind determining this.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Fuses in parallel
PostPosted: Fri Dec 15, 2023 10:47 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 487
Location: Indiana
To calculate fuse size you need to know what you are protecting. Are you trying to protect a transformer? A feeder? What size? What type of fuse or fuse holder? What type of switchgear will the fuses be installed in?

I haven't seen a triple barrel fuse before either but it appears that you can buy them in CL-14. I only see up to 300E though. If you think you need 360E (x3=1080??) then it must not be a CL-14.

Are you in the US or is this somewhere else? Is this existing switchgear or new? Do you have any cut sheets on the gear? Any other information?

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883