Author |
Message |
Tboy01
Post subject: Under calibrated PPE? Posted: Wed Mar 01, 2023 9:51 am |
Hello everyone,
I am new to the forum. I would like to ask ,in what way is 25 cal/cm2 arc protected clothing possible to be classified 2.cat.
Thanks for your help Tibor
Top |
mayanees
Post subject: Re: Under calibrated PPE? Posted: Mon Mar 06, 2023 10:51 am |
Joined: Tue Feb 17, 2009 8:38 am Posts: 61 Location: Westminster, MD
70E Table 130.7(C)15(c) Personal Protective Equipment is the table used for the PPE Categories method. In that Table PPE 1 goes to 4 cals, PPE 2 goes to 8 cals, PPE 3 - 25 cals and PPE 4 - 40 cals. Category 2 is good for 8 calories, but anything larger can be used for a lower incident energy rating, so a 25-cal PPE can be used for Cat 2.
Top |
Tboy01
Post subject: Re: Under calibrated PPE? Posted: Mon Mar 06, 2023 12:39 pm |
mayanees wrote: 70E Table 130.7(C)15(c) Personal Protective Equipment is the table used for the PPE Categories method. In that Table PPE 1 goes to 4 cals, PPE 2 goes to 8 cals, PPE 3 - 25 cals and PPE 4 - 40 cals. Category 2 is good for 8 calories, but anything larger can be used for a lower incident energy rating, so a 25-cal PPE can be used for Cat 2. Thank you for your reply, So, a cloth is marked with 25 cal/cm and 2 CAT. Which one is relevant?
Top |
mpparent
Post subject: Re: Under calibrated PPE? Posted: Mon Mar 06, 2023 3:10 pm |
Might be helpful to take a picture of the tag and post it here.
Top |
Tboy01
Post subject: Re: Under calibrated PPE? Posted: Thu Mar 09, 2023 12:58 am |
mpparent wrote: Might be helpful to take a picture of the tag and post it here.
Attachments: |
File comment: There is an explanation
Top |
mpparent
Post subject: Re: Under calibrated PPE? Posted: Thu Mar 09, 2023 12:35 pm |
Does the garment have a tag on the inside, indicating its ATPV?
Top |
Tboy01
Post subject: Re: Under calibrated PPE? Posted: Fri Mar 10, 2023 12:45 am |
mpparent wrote: Does the garment have a tag on the inside, indicating its ATPV? Yes, ATPV25 cal/cm2 IEC61482 1-2 NFPA 70
Top |
MarkusK
Post subject: Re: Under calibrated PPE? Posted: Fri Mar 10, 2023 1:15 am |
Joined: Wed Dec 12, 2018 12:59 am Posts: 11 Location: Germany
Tboy01 wrote: mpparent wrote: Does the garment have a tag on the inside, indicating its ATPV? Yes, ATPV25 cal/cm2 IEC61482 1-2 NFPA 70 The class 2 refers to APC 2 (Arc Protection Class 2) according to IEC61482-1-2 (european Box Test) and is independent from the ATPV value
Top |
Tboy01
Post subject: Re: Under calibrated PPE? Posted: Fri Mar 10, 2023 2:33 am |
MarkusK wrote: Tboy01 wrote: mpparent wrote: Does the garment have a tag on the inside, indicating its ATPV? Yes, ATPV25 cal/cm2 IEC61482 1-2 NFPA 70 The class 2 refers to APC 2 (Arc Protection Class 2) according to IEC61482-1-2 (european Box Test) and is independent from the ATPV value Yes, it's clear. I needed confirmation that I did indeed need to replace the protective clothing. Thank you for the time you have spent on this topic Sincerely Tibor
Top |