| Author |
Message |
makoester1
Post subject: Short Circuit Study - Motor Contribution Posted: Tue May 10, 2022 3:05 am |
When developing a model in order to run short circuit analyses, is it recommended to group LV motors <50HP? Upon looking at IEEE 399 and IEEE 551, this appears to be typical. Are individuals utilizing this technique or modeling all LV motors individually?
Thanks for the input.
| Top |
mpparent
Post subject: Re: Short Circuit Study - Motor Contribution Posted: Tue May 10, 2022 6:23 am |
I would use the red book as your go-to source, along w/ the purple/violet book. Per the red book, small motors are lumped into one "motor source" from a modelling perspective.
| Top |
nickbramhall
Post subject: Re: Short Circuit Study - Motor Contribution Posted: Tue Jul 12, 2022 1:03 pm |
Joined: Thu Apr 21, 2022 1:00 am Posts: 1 Location: Scotland, UK
Hello, I'm in the UK where we typically run short circuit studies in accordance with IEC 60909. That standard suggests that "for simplification of the calculation" groups of asynchronous low-voltage motors "may be combined to a single equivalent motor". We generally follow this advice with our modelling and combine LV motors at each switchboard or MCC.
However, if there is a particularly large LV motor that may dominate a scenario (for example, an electric driven fire pump that is online when the system is in emergency mode) then we do model that as a standalone motor so we can switch it in/out as necessary.
Combining LV motors also reduces the task of data collection! We typically only ask for detailed motor data for the largest LV motors - this is in case we need to add them for a particular scenario, or for use in other studies such as coordination.
_________________ Nick Bramhall, CEng safearc.co.uk
| Top |
[ 3 posts ] |