I intrepret NFPA 70E110.9(D) to allow me to reduce the instantaneous trip value of a circuit breaker, as done in device coordination, to also reduce incident energy.

What keeps me from reducing to a minimum value (with calculations done) to a minimum when performing work and then resetting when done.

There are add on devices now on the market that do just that.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Thu Mar 26, 2009 2:09 pm 
Sparks Level

Joined: Sun Dec 23, 2007 1:44 pm
Posts: 348
Location: Charlotte, NC
We generally refer to those as maintenance settings for the specific purpose you are asking about. Depending on the breaker and associated overcurrent protection you have, it might have an alt settings available. If so you can use the front panel or an external switch to enable them once configured. You could lower your pickup, time delay, and inst. if necessary. And you are correct about the other devices available if your relay does not allow it.

You could also look at the entire facility (if practical) to see if you could modify the settings permanently as they may be elevated now just to insure against nuisance tripping without regard to arc flash issues.

Don't usually like the idea of "dialing it down" by hand since it may not get back to the correct setting after the work is done.

There are other posts here about this very issue if you can find them.

Hope it helps.


Top
 Profile Send private message  
Reply with quote  
 Post subject:
PostPosted: Fri Mar 27, 2009 4:18 am 

Joined: Mon Dec 08, 2008 7:52 pm
Posts: 8
Thanks for the reply

Good points. I would not suggest this to our guys just seems too easy and too easy to make the wrong assumptions once the setting is made.


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883