 Post subject: Grounding.....
PostPosted: Fri Aug 26, 2016 8:32 am 
User avatar

Joined: Mon Nov 05, 2007 10:10 am
Posts: 48
Location: Mid-West
Looking at the IE calculation there is a variable for grounding depending on what type system you have installed, and noticed that the grounding type can have a significant effect on the calculated IE energy on ungrounded vs grounded systems. Just curious if anyone can shed some light or point me in the direction of some literature that would better explain the cause of increased IE on ungrounded systems. I see the variable change in the calculations and there is a brief statement about this and found some articles that discuss the grounding types etc. but could not find any technical literature on the “why’s” any information is greatly appreciated. Thanks…


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Grounding.....
PostPosted: Fri Aug 26, 2016 8:52 am 
Plasma Level
User avatar

Joined: Tue Oct 26, 2010 9:08 am
Posts: 2178
Location: North Carolina
I've seen some reports that anecdotally mention that they do NOT see any differences compared to the IEEE 1584 calculation. It might be simply a numerical anomaly or not. The calculation itself is purely an empirical curve fit so there is no theoretical explanation as to any physical meanings behind the IEEE 1584 empirical equation because by nature, there isn't one.

The article below is actual testing that tested the ungrounded/resistance grounded concept and found that you get a 3 phase arcing fault but that the A-C fault is actually more like A-N-B where N is the surrounding housing. Given that in a solidly grounded system it can just as form A-G or C-G as the third arc and there is no need for a double line-to-ground fault (LGL), the reduction in the amount of arcing columns might provide some explanation here. Obviously impedance (through the grounded connections) plays a role for the third and fourth arcs. This is purely a guess on my part. I have no documentation to back it up.

http://www.neiengineering.com/wp-conten ... esting.pdf


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Grounding.....
PostPosted: Sat Aug 27, 2016 3:39 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1725
Location: Scottsdale, Arizona
It was more of the erratic nature of the 3 phase arcing current getting established. It it didn't always initially act as a "balanced" three phase event even though the calculations assume all three phases are equal. The IEEE 1584 Working Group has been looking into this but at the moment I'm not able to say much else. Stay tuned!


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 3 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883