Quote:
We have been trying to figure out where OSHA says you have to perform an arc flash study. Is this requirement actually in there?
Arc Flash studies are not a requirement. However when the study is not preformed, the task tables must be used in the back of the NFPA-70E.
Quote:
Right now, IEEE 1584 is the calculation method that people use when conducting studies.
There are 2 methods for calculating Arc Flash, while the IEE1584 is 1, the math in the NFPA-70E is different and shows different results. This is a great source of debate since different PPE is required by both results.
Quote:
It looks like the new 2008 NFPA 70E might be putting more weight on calculations
The revised NFPA-70E will be coming out in 2009, with additional Task tables and a revised version of Arc Flash, which reads:
Flash Hazard. A dangerous condition associated with the possible release of energy caused by an electric arc.
FPN No. 1: A flash hazard may exist when energized electrical conductors or circuit parts are exposed or when they are within equipment in a guarded or enclosed condition, provided a person is interacting with the equipment in such a manner that could cause an electric arc.
Per the FPN, the hazard is considered to exist if energized parts are exposed or a person is interacting with the equipment IN SUCH A MANNER TO CAUSE AN ELECTRIC ARC. Not all interaction with energized equipment will cause an electic arc. Need to be careful how this is interpreted. Racking a breaker certainly would fit the bill, but I don't think resetting a breaker would.
Simply put......an Employee must wear the appropriate PPE to delatch or relatch the Equipment, regardless of covers, guards & shields.
Additionally I hear that due to garment improvements, cotton underwear "maybe" removed from the Dupont clothing standard.Just my $.02