Frank wrote:
Does bus differential protection reduce the clearing time for an arcing fault and should this be considered in performing the arc flash calculations?
Jim is Correct. Differential protection of a "bus" is protection and should not care whether the fault is arcing or bolted. Simply stated the differential sensing zone is bounded by the CTs used to measure the currents in and out of the zoneand the protected circuit is that which is disconnected from sources by the controlled circuit breakers. Note that in differential protection all CBs bounding the zone could be opened including those being fed by regenerative sources such as large motors.
Important to understand the response time of differential protection based on the fault currents expected. Consult the rely manufacturer to udnerstand all relevant considerations. Note that in LV systems the range of currents that have to be dealt with is significant and that creates application complexity. But, generally very fast response is possible.
When using 87T (transformer differential) need to make sure that the requirement to get around inrush currents do not negatively impact AF protection on the secondary circuits.
One interesting application for secondary substation protection with one relay is where an 87T function is used to protect the transformer and immediate conductors, but a 50/51 function within the same relay is used to protect the secondary conductors that are downstream of the secondary CT location but may be ahead of a secondary Main CB. Digital relays are available that can do this. May be useful where the secondary switchgear is too far from the transformer to easily include it in the zone of protection or where the CTs necessary for differential protection cannot be located within the LV gear for any of various reasons.
Analytical software, to my knowledge, does not normally model 87 protection via traditional curves, however the clearing time (sensing+relay response + CB responce/clearing) can be entered into the analysis. Note that in LV CBs operated via shunt trip some additional time must be added for the shunt trip versus the internal flux shifter normally used by the integral trip.