Ed Pramik wrote:
I have some clients who get their low voltage from a utility owned transformer. In the past I have been able to get the transformer and primary fuse data from the utility so I can model and calculate incident energy at the secondary main breaker (customer owned) as well as provide coordination. Lately the utilities are no longer giving me this information. They will only provide short circuit data at the point of common coupling. My guess is that the utility does not want to be liable for their protective devices working to provide arc flash protection at the customer's equipment.
Don't make the assumption that what one person at a utility says has any relation to what another will in terms of policy. I usually deal with one, very large utility in california. Depending on who I talk to, I have been told that
1:They really are not sure what equipment they have in that area
2:THey pull a number off of a table they have that is based on service entrance rating
( which frequently has no relationship to the serving transformer size)
3: That I will have to fill out an application and pay $500 to get that information.
(That turned around ABRUPTLY when I asked for the exact tarrif that allowed for that charge.
But I have been hit with that from one particular district several times.)
4: Exact transformer size, impedance, complete upstream fault information for either of the two alternate sources, transformer fuse information and upstream relay information for the two possible sources.
In the case of 1: above, I think the guy was being honest. THat was a part of their system that has elements dating back to the thirties, if not the twenties, and they still prvide DC and Steam to some clients, in a congested urban area.
2: is a problem. In one project I am working on now (OK waiting for submittials on) the utility has given me a fault number that is larger than the new transformer they are putting in will allow, even if they have an infinite bus, and ANY reasonable impedance.