Aleesha M. Angard wrote:
Hi All,
As our interim measure while we are process of performing an Arc flash analysis study for our facility we have decided to use the NFPA 70E tables (2012 version) to guide PPE requirements for different types of work/tasks being done on the MCC/ Switchgear. However, the tables are accompanied by parameters which state values such as the available short circuit current, FCT etc. Our gear at the 480V and >1kV level for example, may not necessarily follow these parameters. An example of this is at our 480V level, our FCT for our protective devices are greater than those stated in the parameters. Would it be wise to use these tables given that the parameters do not match ours?
Another issue we have is around the use of the term "exposed energised conductors or circuit parts" in the parameters. If you are familiar with the Freedom 2100 Cutler Hammer MCCs, when the cubicle door is open, there are shutters which guard the bus. Can we say there are "exposed" parts in this case?
Appreciate any kind of dialogue on this!!!
Hi Aleesha,
I believe your scenario is somewhat similiar to my original question below. Have a read on that thread and think again.
http://www.arcflashforum.com/threads/1783/#post-8672 We have decided as a company to move forward with classifying the starter the same category as the MCC bus. This is mainly due to insufficient information provided by supplier, mainly the MCCB manufacturer as nobody will gurantee you it is not consider exposed.
Cheers,
Brandon