PaulEngr wrote:
Below 300 V, 70E says "avoid contact" but does not specify what that is. Some folks are interpreting this to mean insulated tools. If this were not so then all the 70E sections talking about insulated tools really have no practical purpose.
Paul,
Just to play devil's advocate...
If I look at table 130.7(c)(15)(a) there is a column for "rubber insulating gloves" and another for "insulated and insulating hand tools". From looking over the 8 scenarios provided in the category of <240 volts, it certainly seems the intent is to require the use of rubber insulating gloves (and tools) when you are putting your hands near live unprotected parts, which would include tasks such as voltage testing. The tasks that do not require the insulated gloves all either have some sort of assumed distance between the person's hands and the live parts, or covers on. For example you can remove a bolted cover to expose live wires with no gloves, but as soon as you need to work on the live wires, or do voltage testing, then you need the gloves on.
Agree or disagree?