Author:  Noah [ Fri Dec 07, 2012 12:44 pm ]
Post subject:  CSA Z463

A new standard Z463 is available for the maintenance of electrical system. Anyone has reviewered the standards and how much it impacts arc flash study from Z462?

Author:  Terry Becker [ Mon Dec 17, 2012 6:48 am ]
Post subject: 

It doesn't impact your engineering incident energy analysis study at all. I am on the CSA Z463 Technical Committee. CSA Z463 will emphasize the need for some form of electrical equipment maintenance to be completed in an effort to manage the accuracy of the calculations performed. This would be applicable to protection and coordination as well.

People need to realize that this whole thing is not about "arc flash." Electrical shock is the higher risk of exposure to all workers on a worksite. The probability of an arcing fault and and an arc flash occurring was and is low.

Do you have an Electrical Safety Program in place?

Author:  Noah [ Thu Dec 20, 2012 9:22 am ]
Post subject: 

Thanks Terry! We are a consultant company and one of our business is to provide Arc flash hazard analysis for our clients.