| Author |
Message |
|
MarkColby
|
Post subject: 2009 NFPA 70E errors - how to report them Posted: Fri Jan 23, 2009 1:15 pm |
|
Joined: Fri Jan 23, 2009 1:10 pm Posts: 1
|
|
I was just comparing the NFPA 70E (2009) to Canadian Z462-08 and noticed that in the NFPA 70E on page 70E-25, in Table 130.2(C), the "Restricted Approach Boundary (column (4)) that many of the metric distances are incorrect. Someone made an error when converting from feet/inches to meters or mm.
The Z462-08 is correct in all of their conversions (see Dec 08 Z462-08 page 34, Table 1).
The NFPA 70E is wrong.
|
|
| Top |
|
 |
|
Jim Phillips (brainfiller)
|
Post subject: Posted: Sat Mar 07, 2009 8:18 am |
|
| Plasma Level |
 |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1727 Location: Scottsdale, Arizona
|
|
Mark,
As we discussed on the telelphone, you are correct, there are a few numbers that are off a bit. I checked with one out at our last 1584 meeting and it was suggested that you or someone submit a proposal to change it in the next Edition of 70E. That's about the only way to make sure it is addressed.
Good Catch!
_________________ Jim Phillips, P.E. Brainfiller.com
|
|
| Top |
|
 |
|
Ralpa494
|
Post subject: Posted: Thu Mar 12, 2009 6:34 am |
|
Joined: Tue Feb 24, 2009 5:06 pm Posts: 3 Location: SE Wisconsin
|
|
| Top |
|
 |
|
Page 1 of 1
|
[ 3 posts ] |
|
|