| Author: | Cfoland [ Thu Mar 27, 2025 9:21 am ] |
| Post subject: | Arc Rating and Stoll curve |
I have received conflicting information on arc ratings from two people I respect in the industry. This concerns wearing the minimum required PPE when using the incident energy analysis method 130.5(G) and T130.5G and informational, note 2 & 3 for the definition Arc Rating. The first piece of information is that if you wear the minimum PPE, you have a 50% chance of getting a second-degree burn, so never dress to the minimum. The second piece of information is that this is not how the stoll curve is meant to be applied, and wearing the minimum PPE will not get you burned if the incident energy does not exceed the PPE rating. On a side note, are manufacturers permitted to give the clothing an arc rating higher than that of their lowest-tested specimen? Is this a concern? Informational Note No. 2: ATPV is defined in ASTM F1959/F1959M, Standard Test Method for Determining the Arc Rating of Materials for Clothing, as the incident energy (cal/cm2) on a material or a multilayer system of materials that results in a 50 percent probability that sufficient heat transfer through the tested specimen is predicted to cause the onset of a second degree skin burn injury based on the Stoll curve. |
|
| Author: | mpparent [ Thu Mar 27, 2025 9:54 am ] |
| Post subject: | Re: Arc Rating and Stoll curve |
I don't know this for a fact, but as you may know, some manufacturers will list, for example, a suit with a 40 cal/cm^2 rating. But when inspecting the tag, you'll see an arc rating of 45 cal/cm^2. I always thought this was to cover the 50% break-thru (for 40 cal/cm^2), but I have never asked the question. Mike |
|
| Page 1 of 1 | All times are UTC - 7 hours |
| Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group http://www.phpbb.com/ |
|