Hello everyone,

I am new to the forum.
I would like to ask ,in what way is 25 cal/cm2 arc protected clothing possible to be classified 2.cat.

Thanks for your help
Tibor


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Under calibrated PPE?
PostPosted: Mon Mar 06, 2023 10:51 am 
Sparks Level

Joined: Tue Feb 17, 2009 8:38 am
Posts: 62
Location: Westminster, MD
70E Table 130.7(C)15(c) Personal Protective Equipment is the table used for the PPE Categories method. In that Table PPE 1 goes to 4 cals, PPE 2 goes to 8 cals, PPE 3 - 25 cals and PPE 4 - 40 cals.
Category 2 is good for 8 calories, but anything larger can be used for a lower incident energy rating, so a 25-cal PPE can be used for Cat 2.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Under calibrated PPE?
PostPosted: Mon Mar 06, 2023 12:39 pm 

Joined: Wed Mar 01, 2023 8:28 am
Posts: 5
mayanees wrote:
70E Table 130.7(C)15(c) Personal Protective Equipment is the table used for the PPE Categories method. In that Table PPE 1 goes to 4 cals, PPE 2 goes to 8 cals, PPE 3 - 25 cals and PPE 4 - 40 cals.
Category 2 is good for 8 calories, but anything larger can be used for a lower incident energy rating, so a 25-cal PPE can be used for Cat 2.


Thank you for your reply,
So, a cloth is marked with 25 cal/cm and 2 CAT.
Which one is relevant?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Under calibrated PPE?
PostPosted: Thu Mar 09, 2023 12:58 am 

Joined: Wed Mar 01, 2023 8:28 am
Posts: 5
mpparent wrote:
Might be helpful to take a picture of the tag and post it here.

Mike


Attachments:
File comment: There is an explanation
Képernyőkép 2023-03-09 085347.jpg
Képernyőkép 2023-03-09 085347.jpg [ 166.36 KiB | Viewed 47725 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Under calibrated PPE?
PostPosted: Fri Mar 10, 2023 12:45 am 

Joined: Wed Mar 01, 2023 8:28 am
Posts: 5
mpparent wrote:
Does the garment have a tag on the inside, indicating its ATPV?

Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Under calibrated PPE?
PostPosted: Fri Mar 10, 2023 1:15 am 

Joined: Wed Dec 12, 2018 12:59 am
Posts: 12
Location: Germany
Tboy01 wrote:
mpparent wrote:
Does the garment have a tag on the inside, indicating its ATPV?

Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70


The class 2 refers to APC 2 (Arc Protection Class 2) according to IEC61482-1-2 (european Box Test) and is independent from the ATPV value


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Under calibrated PPE?
PostPosted: Fri Mar 10, 2023 2:33 am 

Joined: Wed Mar 01, 2023 8:28 am
Posts: 5
MarkusK wrote:
Tboy01 wrote:
mpparent wrote:
Does the garment have a tag on the inside, indicating its ATPV?

Yes,
ATPV25 cal/cm2
IEC61482 1-2
NFPA 70


The class 2 refers to APC 2 (Arc Protection Class 2) according to IEC61482-1-2 (european Box Test) and is independent from the ATPV value


Yes, it's clear.
I needed confirmation that I did indeed need to replace the protective clothing.
Thank you for the time you have spent on this topic

Sincerely
Tibor


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883