stevenal wrote:
Perhaps they were attempting consistency with NESC, which does not require arc rated clothing below 2.0 cal/cm^2 IE. I'm unaware of the science behind it, though.
Currently (2012) NESC reads:
NESC 410A.3 "If the assessment determines a potential employee exposure greater than 2 cal/cm2 exists (see Neal, Bingham, and Doughty [B63]), the employer shall..." do a detailed analysis or use the tables in NESC and then wear appropriate PPE.
The tables in section 410 only support a 4 cal or higher clothing system. There is no mention of 1.2 cal/cm^2 or 2 cal/cm^2 anywhere in the tables.
So I can understand the desire to reconcile the range of 1.2 to 2.0 cal/cm^2 (and that's the question I'm asking!) but I'm not seeing support for it. I know that during the last NESC Code cycle there was strong discussion about dropping this standard down to 1.2 cal to match other standards.