It is currently Wed Oct 15, 2025 12:43 pm



Post new topic Reply to topic
Author Message
 Post subject: Advice on how to approach prohibitive AF values at MDP
PostPosted: Tue Jul 29, 2025 2:17 pm 

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 26
I've heard it stated by AF study engineers something to the effect of: 'if a label shows an astronomic calorie value, it's clear the person doing the study has no idea what they're doing'.

That said, what approach(es) do you all take when an existing system has particular components that have obscenely high incident energy levels? This is particularly common with smaller commercial Main Service Distribution gear, where the available energy from the utility to the entire busing is orders of magnitude higher than any PPE accounts for (in my current study, I'm talking excess of 10kcal on a 480V, 400a service). The feeder busing runs through each section of the MDP so the sticker needs to reflect what's there.

The only 'parlor trick' I know of is the 2-second rule, which drops the incident energy down to 22.9 cal, but given it's in a small room with one (crash bar-equipped) door, I'm hesitant to apply it here. Seen too many safety videos of electricians getting blown up. I guess my question is, how would you approach the customer with this situation?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Advice on how to approach prohibitive AF values at MDP
PostPosted: Wed Jul 30, 2025 4:28 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 438
Location: Indiana
I wish I still had access to and permission to share some of the video evidence I was privy to when I was doing forensic/expert witness work for fires and explosions suspected of an electrical cause. Once case from a few years ago involved a fault at the line side of a 480V, I think 3000A from memory, switchboard. Might have been 2500A or even 4000A. I just don't recall now. It was fed from two utility company transformers in a vault in a spot network configuration.

The switchboard was in a room roughly 20-25' wide and maybe 40-50' long with a 15'+ high ceiling (floor slab of floor above). It was a fairly large room with a lot of other electrical and mechanical equipment in it. Corridor video surveillance captured the event. At least what it looked like from outside the mechanical/gear room. Their was a pair of locked, solid wooden, steel framed, commercial type double doors from the corridor into the gear room. These doors were roughly 20' away from the main breaker section of the switchboard. The corridor doors blew open, ripping the deadbolt out of the door and a giant fireball erupted from the room. I mean giant. Again, about 20' away from the gear. Some of the bolt-on panels of the gear were blown out and very deformed of course. If a person happened to be anywhere in that room during the event, not just within the limited approach boundary, and who knows what the calculated arc flash boundary was, I think they would have been lucky to survive. The whole room had to have been engulfed. The pressure wave blew out several of the corridor lay-in ceiling tiles.

If those engineers that claim high incident energies mean someone doesn't know what they are doing saw that video I think they would change their minds.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Advice on how to approach prohibitive AF values at MDP
PostPosted: Thu Aug 28, 2025 3:32 pm 

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 26
bbaumer wrote:
I wish I still had access to and permission to share some of the video evidence I was privy to when I was doing forensic/expert witness work for fires and explosions suspected of an electrical cause. Once case from a few years ago involved a fault at the line side of a 480V, I think 3000A from memory, switchboard. Might have been 2500A or even 4000A. I just don't recall now. It was fed from two utility company transformers in a vault in a spot network configuration.

The switchboard was in a room roughly 20-25' wide and maybe 40-50' long with a 15'+ high ceiling (floor slab of floor above). It was a fairly large room with a lot of other electrical and mechanical equipment in it. Corridor video surveillance captured the event. At least what it looked like from outside the mechanical/gear room. Their was a pair of locked, solid wooden, steel framed, commercial type double doors from the corridor into the gear room. These doors were roughly 20' away from the main breaker section of the switchboard. The corridor doors blew open, ripping the deadbolt out of the door and a giant fireball erupted from the room. I mean giant. Again, about 20' away from the gear. Some of the bolt-on panels of the gear were blown out and very deformed of course. If a person happened to be anywhere in that room during the event, not just within the limited approach boundary, and who knows what the calculated arc flash boundary was, I think they would have been lucky to survive. The whole room had to have been engulfed. The pressure wave blew out several of the corridor lay-in ceiling tiles.

If those engineers that claim high incident energies mean someone doesn't know what they are doing saw that video I think they would change their minds.

Circling back to this (and touching on a common theme talked about here), when a study indicates a generator breaker will never trip because the fault current is below 2kA (causing it to time out in software), what are the options? In a study I'm working on now, the LT pickup is 320A, the ST pickup is 3200A, and the INST is 7200A(fixed). How does one determine how far one could drop the ST pickup before I'm in danger of tripping under inrush conditions of downstream pumps?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Advice on how to approach prohibitive AF values at MDP
PostPosted: Thu Aug 28, 2025 4:42 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 438
Location: Indiana
Add the pump motor starting curve to the TCC and coordinate the breaker with the curve.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Advice on how to approach prohibitive AF values at MDP
PostPosted: Fri Aug 29, 2025 3:11 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 438
Location: Indiana
For example

Attachment:
GENERATOR AND PUMP ONE-LINE.jpg
GENERATOR AND PUMP ONE-LINE.jpg [ 139.52 KiB | Viewed 5404637 times ]


Attachment:
PUMP MISCOORDINATION1.jpg
PUMP MISCOORDINATION1.jpg [ 583.12 KiB | Viewed 5404637 times ]


Attachment:
PUMP COORDINATION1.jpg
PUMP COORDINATION1.jpg [ 586.07 KiB | Viewed 5404637 times ]

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Advice on how to approach prohibitive AF values at MDP
PostPosted: Tue Sep 02, 2025 11:30 am 

Joined: Fri Mar 28, 2025 2:54 pm
Posts: 26
bbaumer wrote:
Add the pump motor starting curve to the TCC and coordinate the breaker with the curve.


Thank you! In this particular case, the generator breaker and ATS are the points with objectionable incident energy, but there is an MCC feeding 3 motor circuits downstream and a 480V panel>transformer>208V panel situation (feeds no motors). Only one of the three motors has a VFD (which also has an RL reactor upstream, but no maintenance bypass).

Would you, in such a case, add the inrush current of the two non-VFD-controlled motors together, along with the inrush of the transformer, and adjust the curve to the sum?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Advice on how to approach prohibitive AF values at MDP
PostPosted: Thu Sep 04, 2025 9:47 am 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 438
Location: Indiana
NeDCE wrote:
bbaumer wrote:
Add the pump motor starting curve to the TCC and coordinate the breaker with the curve.


Thank you! In this particular case, the generator breaker and ATS are the points with objectionable incident energy, but there is an MCC feeding 3 motor circuits downstream and a 480V panel>transformer>208V panel situation (feeds no motors). Only one of the three motors has a VFD (which also has an RL reactor upstream, but no maintenance bypass).

Would you, in such a case, add the inrush current of the two non-VFD-controlled motors together, along with the inrush of the transformer, and adjust the curve to the sum?


Maybe. Not enough information. I can for sure model multiple motors on one feeder thereby combining their starting curves into one. I'm not sure if that is possible to add in the transformer inrush too. I might be able to build that into the controller but I've never tried. Also sizes of each would affect how I would approach it.

_________________
SKM jockey for hire
PE in 17 states


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 7 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883