abinadi wrote:
Without a utility OCPD, the software I am using for arc flash modeling will not calculate an incident energy for the first bus (which is usually the main circuit breaker). How do I label that panel without a calculated incident energy? Does anyone else run into this problem?
not sure which arc flash analysis program you are using but I would expect you can apply IEEE 1584 two (2) seconds rule by manually specifying arc duration if OCPD information is missing. In case when it takes OCPD more than 2 sec to clear arcing fault, incident energy would be determined based on 2 sec arc duration cutoff. A screenshot below shows an example of it.