Jim Phillips (brainfiller)
|
Post subject: Maximum number of arc flash labels at one location Posted: Sun Jul 18, 2021 10:57 am |
|
| Plasma Level |
 |
Joined: Mon Sep 17, 2007 5:00 pm Posts: 1727 Location: Scottsdale, Arizona
|
|
This week’s question was asked years ago but it keeps coming up. Most recently in a committee technical discussion. It is similar to last week’s question: How should incident energy from arc energy reduction methods be addressed on arc flash labels?
This week’s question is about the number of DIFFERENT LABELS at the SAME LOCATION for different scenarios. i.e. a label for normal, a label for maintenance mode, a label for…. So here goes:
What is the maximum number of DIFFERENT arc flash labels have you seen/used at the SAME location?
1 2 More than 2 Doesn’t apply
How many DIFFERENT labels have you seen/used at the SAME location? (read the whole post first)
|
|
| Top |
|
 |
|
JBD
|
Post subject: Re: Maximum number of arc flash labels at one location Posted: Sun Jul 18, 2021 5:22 pm |
|
Joined: Mon Jan 18, 2010 11:35 am Posts: 605 Location: Wisconsin
|
|
I have installed labeling for three different scenarios.
It is amazing what I will do for money.
|
|
| Top |
|
 |
|
Larry Stutts
|
Post subject: Re: Maximum number of arc flash labels at one location Posted: Wed Jul 21, 2021 12:02 pm |
|
| Sparks Level |
 |
Joined: Tue Apr 17, 2012 8:19 am Posts: 253 Location: Charlotte, NC
|
|
When I was doing the labels for the solar power grid tie inverters, there was 1 label for each opening in the inverter enclosure (there are 10 doors / access panels for the enclosure) for the installed production parameters (4 MW transformer, no fuses). There is a second set of labels for testing in our facility for the operational testing parameters (500 kW transformer, with semiconductor fuses, and a breaker disconnect).
|
|
| Top |
|
 |
|
Larry Stutts
|
Post subject: Re: Maximum number of arc flash labels at one location Posted: Wed Jul 28, 2021 8:44 am |
|
| Sparks Level |
 |
Joined: Tue Apr 17, 2012 8:19 am Posts: 253 Location: Charlotte, NC
|
|
to clarify my earlier post: The incident energy ranged from below 1 cal/cm^2 to 75 cal/cm^2, depending on which particular door / panel you opened
|
|