It is currently Mon Jun 22, 2026 11:07 pm



Post new topic Reply to topic

When do you plan on updating arc flash studies based on the 2018 IEEE 1584?
Immediately - ASAP 9%  9%  [ 11 ]
Within 3 months 6%  6%  [ 7 ]
Within 6 months 11%  11%  [ 13 ]
Within a year 5%  5%  [ 6 ]
As part of the NFPA 70E 5-year review 67%  67%  [ 83 ]
Never or does not apply 2%  2%  [ 3 ]
Total votes : 123
Author Message
 Post subject: Time frame to update studies with 2018 IEEE 1584
PostPosted: Sat Dec 08, 2018 3:03 pm 
Plasma Level
User avatar

Joined: Mon Sep 17, 2007 5:00 pm
Posts: 1737
Location: Scottsdale, Arizona
This week’s question was provided by one of our forum members/friends and is quite timely with the recent release of the 2018 Edition of IEEE 1584.

Now that the 2018 Edition of IEEE 1584 has been published, when do you plan on updating your (clients) arc flash studies?

Immediately - ASAP
Within 3 months
Within 6 months
Within a year
As part of the NFPA 70E 5-year review
Never or does not apply


This has been a hot topic of conversation so feel free to share your thoughts and views!


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Time frame to update studies with 2018 IEEE 1584
PostPosted: Mon Dec 10, 2018 11:57 am 

Joined: Thu Sep 27, 2012 3:02 pm
Posts: 19
Location: Washington
What would be the driving requirement for updating studies that aren't due for a review?

Also, what would prevent a client from sticking with the 2002 equations for an existing study when the review period comes up? Are the results going to be significantly different? By "significantly" I mean raising or lowering IE values enough to have to change what PPE is worn.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Time frame to update studies with 2018 IEEE 1584
PostPosted: Tue Dec 11, 2018 7:33 am 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
Spryduck wrote:
Are the results going to be significantly different? By "significantly" I mean raising or lowering IE values enough to have to change what PPE is worn.


Yes indeed the results could be way different. Screenshots below show calculation results for a similar system as predicted by IEEE 1584 - 2002 (Arc Flash Analytic version 5.0)

Image

and by new IEEE 1584 - 2018 (Arc Flash Analytic version 6.0)

Image

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Time frame to update studies with 2018 IEEE 1584
PostPosted: Tue Jan 22, 2019 4:17 pm 

Joined: Tue Jan 22, 2019 3:56 pm
Posts: 1
Here's a comparison between 1584 2002 vs 2018 on a sample project. Results are pretty similar, although typical box dimensions are used. YMMV.

Johnny Ma
SKM Systems Analysis, Inc.

Image
Image


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883