| Author: | Jim Phillips (brainfiller) [ Sun Aug 29, 2010 4:00 pm ] |
| Post subject: | Utility Short Circuit Current |
When performing an arc flash calculation study do you use the normal condition fault current only or do you also look at alternate scenarios such as minimum or maximum fault current? |
|
| Author: | acobb [ Mon Aug 30, 2010 8:42 am ] |
| Post subject: | |
I voted that we consider alternate scenarios, but this is for (NESC) OH utility distribution lines where work will be performed at locations certainly other than the substation bus. |
|
| Author: | Gary B [ Wed Oct 06, 2010 9:53 pm ] |
| Post subject: | |
I have manipulated the local PUD substation power transformers on and off line (only within the software Most locations I would not have access to information to do this but at this one spot I had previously completed work for the PUD. |
|