I would suggest that you create an "Arc Flash & Shock Warning Label Schedule," that would be part of your Electrical Safety Program.
This document contains the specification for you simple Standard label that would comply with Article 110.16 in the US and Rule 2-306 in Canada.
Also included in this document would be an orthographic block diagram of SWGR and an MCC, and you indicate where you want the labels applied and the height you want them applied.
I have seen quite a few sites with more than 10 MCC Buildings/Electrical Swithc Houses and the labels are all in different locations because a Labeling Schedule was not provided to the EPCM (to make sure the detailed labels are all the same) and the contractor who installed the labels.
As well this Labeling Schedule would be used everytime you expand your Plant, etc...
It is a specification for Arc Flash & Shock Warning labels.
These are the tools that you need within your Electrical Safety Program for due diligence and to ensure consistent application of the electrical safe work practices it outlines.