 Post subject: Arc Flash Labels over 50V
PostPosted: Wed Sep 11, 2024 6:45 am 

Joined: Wed Sep 11, 2024 6:35 am
Posts: 3
A customer is requesting all their machines that are over 50V to have an arc flash label and assessment done. Typically we will do an arc flash assessment of the disconnect the machines are connected to. These are typically 480V 3 phase. I came across a machine that is plugged into a 120VAC outlet and they want a label on the machine. Could a generic label be used for this situation because there is no likelihood of an arc flash to happen? Does a calculation need to be done?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Labels over 50V
PostPosted: Wed Sep 11, 2024 8:39 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 163
There is no arc flash risk for 120V circuits. So no AF label required.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Labels over 50V
PostPosted: Wed Sep 11, 2024 9:47 am 

Joined: Wed Sep 11, 2024 6:35 am
Posts: 3
mpparent wrote:
There is no arc flash risk for 120V circuits. So no AF label required.

Mike


Thanks for the quick response. That's what I was thinking. Does it say that in the NFPA 70E anywhere?


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Labels over 50V
PostPosted: Thu Sep 12, 2024 6:13 am 
Sparks Level

Joined: Thu Apr 18, 2019 11:42 am
Posts: 163
I don't recall 120V systems specifically called out in 70E has not being capable of an arc flash. However, research indicates it as such. Also, the tables for PPE selection in 70E do not identify 120V systems.

You could look at this link for more info: https://www.70econsultants.com/arc-flas ... nd-208vac/

Also...get yourself a copy of 70E.

Mike


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Arc Flash Labels over 50V
PostPosted: Thu Sep 12, 2024 8:12 am 
Sparks Level

Joined: Fri Sep 28, 2018 7:32 am
Posts: 55
Location: Sioux Falls, SD
I feel this is up to the customer. Electrical hazards must be properly identified. While most refer to the labels as "arc flash labels" these nearly always contain both arc flash and electrical shock information. If the facility does not otherwise identify the enclosures voltage or presence of electrical shock hazard, they may be looking for these labels to do so. A very large customer used a modified version of our arc flash labels to identify the voltage and electrical shock hazard information but stated "NO ARC FLASH HAZARD PRESENT".


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883