I am performing an arc flash study and getting very high incident energy values. A few things I need clarification on:

Arc Duration: Since the main switch is fed by unprotected consumer mains, I have used the 2-second rule for both arc duration and reduced arc duration. Does this approach seem reasonable?

Voltage Selection: I am confused about which voltage to use for short-circuit calculations:

The transformer nameplate voltage is 22kV/433V.
A previous report I reviewed uses 415V for calculations.
IEC 60038 defines the nominal system voltage as 400V.
Which voltage should be used for short-circuit calculations in IEC 60909-based fault analysis and for arc flash energy calculations?

Attached is my arc flash study report, showing high incident energy values. Would appreciate any guidance on whether my inputs are correct or if I need adjustments.


Attachments:
Arc Flash Analysis.png
Arc Flash Analysis.png [ 96.86 KiB | Viewed 73689 times ]
Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Client Transformer Information
PostPosted: Sun Mar 02, 2025 2:30 pm 
Arc Level
User avatar

Joined: Fri Jul 08, 2016 10:01 am
Posts: 499
Is this a pad mounted transformer?

If so, you might want to view this video and get th white paper in the description as well as take note that the NESC ( IEEE C2) says 4 calorie PPE is sufficient for 480V transformers. I don't know if the same applies at your voltage:

https://youtu.be/jKqy9uMfwq4?feature=shared

Also, I'm not surprised at all by your calc results. Video may be helpful.

_________________
Retired but I might visit once in awhile


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883