Helen Workman
|
Post subject: Inclusion of auto transformers in arc flash analysis Posted: Thu Jun 11, 2015 12:10 am |
|
Joined: Wed Jun 10, 2015 11:48 pm Posts: 1
|
|
I am modelling a small 415V network for an arc flash study. Three motors, 1 x 45kW and 2 x 90kW are started via an auto-transformer starter.
Will the auto-transformer contribute anything to the arc flash study, or can I look at a worse case scenario, and consider the motors starting DOL?
If the auto-transformer needs to be included in the study - what characteristics do I need to include?
|
|
| Top |
|
 |
|
PaulEngr
|
Post subject: Re: Inclusion of auto transformers in arc flash analysis Posted: Thu Jul 02, 2015 10:30 pm |
|
| Plasma Level |
 |
Joined: Tue Oct 26, 2010 9:08 am Posts: 2178 Location: North Carolina
|
|
Shouldn,'t add anything if its out of the circuit during normal operating conditions.
|
|