I have two single phase 480V-120V 75KVA 5.0% Impedance transformers, 625A secondary. They are connected as boosting autotransformers in open delta, 480V primary, 600V secondary.
I need to calculate fault current on the secondary. The equivalent transformer capacity would be 625A x 600V x1.73 = 469KVA
But I'm not sure how to calculate the equivalent impedance.
Any direction to reference material or a mathematical method is appreciated. I am not in a position to physically measure impedance by shorting the secondaries and varying input voltage.
gary
|
|
Top |
|
 |
haze10
|
Post subject: Re: Calculate %Z autotransformers in open delta? Posted: Tue May 05, 2015 9:41 am |
|
Joined: Thu Jan 10, 2008 8:49 pm Posts: 520 Location: New England
|
Correction: Equivalent KVA = (75+75) x2 x.86 = 258KVA
|
|
Top |
|
 |
engrick
|
Post subject: Re: Calculate %Z autotransformers in open delta? Posted: Mon May 11, 2015 10:02 am |
|
Joined: Fri Apr 15, 2011 7:43 am Posts: 178 Location: Colorado
|
|
Top |
|
 |
|