wbd wrote:
OSHA does mention in the standard that the dielectric breakdown of air is 10kV per inch. This would give some indication that if the phases are outside this range would that be sufficient?
Nope. That's at atmospheric temperatures. The dielectric breakdown of air rapidly declines as temperature increases.
In a closed enclosure you can easily heat up all the air inside and get multiple arcs everywhere. That's what I typically see post-mortem when a tracking fault gets out of control.
In open air though that's about it. Reasonable phase spacing for open air would seem to hold to prevent arcs for going 3-phase. IEEE 1584 gives 3 phase open air arc gap data up to 153 mm (6"). After that point ehy couldn't maintain a stable arc. That seems reasonable for 5 kV spacing, and I've seen equipment down to 4" phase spacing at 5 kV but up to 15 kV, I tend to be more conservative than that.
There is a lot of data on the subject of how close you need to get before a flashover occurs in IEEE 516, which is what the shock tables in OSHA 1910.269 as well as NESC are based on. The data also includes multipliers for temperature and pressure which would apply.