 Post subject: Utility Fault Values
PostPosted: Sat Dec 10, 2022 7:12 am 

Joined: Mon Aug 17, 2020 8:38 am
Posts: 15
I have a local utility that gave me maximum and minimum fault current values which is rare but nice. The problem is the maximum on 12,470 is around 5000 amps and the minimum is only 177 amps. The minimum values give terrible arc flash ratings for the equipment in the plant I am working in. Does this value seem right? I would think they have more than that value on the feeder in any given day under normal operating conditions. Thanks


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: Utility Fault Values
PostPosted: Thu Dec 15, 2022 9:20 am 
Plasma Level
User avatar

Joined: Wed May 07, 2008 5:00 pm
Posts: 881
Location: Rutland, VT
That minimum fault value seems impossibly low as if you think about it, it is probably lower than the circuit loading. I wonder if they left a zero off and it should be 1770. I would go back and ask them to reconfirm and if you know the full load of the plant, you can convert that to the value at 12.47 and see how close it is to their lowest fault current value.

_________________
Barry Donovan, P.E.
www.workplacesafetysolutions.com


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883