| Location for Elevator Shunt Trip https://brainfiller.com/arcflashforum/viewtopic.php?f=16&t=3642 |
Page 1 of 1 |
| Author: | Kimo [ Wed Mar 04, 2015 6:45 am ] |
| Post subject: | Location for Elevator Shunt Trip |
Could someone direct me to any code/standard (NFPA-70, NFPA-72, ASME A17, IBC, NFPA-101, etc.) that would dictate where the Shunt Trip device Shall be, or that the Elevator Control Disconnecting Means and Shunt Trip Device Shall be the same/integrated device? Thanks! |
| Author: | wbd [ Wed Mar 04, 2015 5:47 pm ] |
| Post subject: | Re: Location for Elevator Shunt Trip |
you may have better response asking this question on a forum that is more geared towards the NEC, such as Mike Holt's forum. this forum is more dedicated and focused on arc flash. |
| Author: | Hurwitz [ Mon Mar 09, 2015 9:25 am ] |
The shunt trip may be in the panel or switchboard supplying the circuit, or it may be in the disonnecting device in the elevator machine room. However, the local elevator code may have more restrictions; you should always check the code of the local jurisdiction. |