| Author: | NeDCE [ Mon Sep 08, 2025 8:40 am ] |
| Post subject: | Modeling different buses in same enclosure (in EasyPower) |
This may be software-specific, maybe not. I'm modeling a multi-sectional MDP wherein a main breaker feeds subsequent sections which are open (i.e. there is no internal arc barricade from one section to the next, so an arc blast in one section will easily travel into the adjacent sections). How would you model this in software? I'm using EasyPower, but the solution may or may not be specific to EasyPower. Normally, the software treats a "bus feeding a breaker feeding another bus" scenario as independent compartments, which is not accurate to the situation. Feel free to ask any questions you need to help flesh this out. |
|
| Author: | mpparent [ Mon Sep 08, 2025 11:49 am ] |
| Post subject: | Re: Modeling different buses in same enclosure (in EasyPower |
Can you model as one bus since it's not sectionalized any way? Mike |
|
| Author: | NeDCE [ Mon Sep 08, 2025 12:26 pm ] |
| Post subject: | Re: Modeling different buses in same enclosure (in EasyPower |
mpparent wrote: Can you model as one bus since it's not sectionalized any way? Mike It's not sectionalized, but there is a main breaker with both line and load side busing. Are you suggesting I model it as one bus only for the incident energy calculations? like creating a separate scenario specifically for the calorie calcs? |
|
| Author: | mpparent [ Tue Sep 09, 2025 6:19 am ] |
| Post subject: | Re: Modeling different buses in same enclosure (in EasyPower |
I am suggesting model as a single bus. In my opinion, line load side bus is irrelevant. Include your main/feeder breakers per field observations. Mike |
|