Post subject: For those that use software from multiple vendors Posted: Tue May 07, 2019 8:21 am |
|
Arc Level |
 |
Joined: Fri Jul 08, 2016 10:01 am Posts: 436 Location: Indiana
|
Just a question out of curiosity mostly for those that have and routinely use SKM, ETAP and Easy Power have you by chance run the same study using the exact same input data in two or all three of the aforementioned software products and if so, was the output identical as far as short circuit and incident energy goes?
_________________ SKM jockey for hire PE in 17 states
|
|
Top |
|
 |
Robertefuhr
|
Post subject: Re: For those that use software from multiple vendors Posted: Mon May 13, 2019 11:38 am |
|
Sparks Level |
 |
Joined: Tue Oct 26, 2010 5:00 pm Posts: 201 Location: Maple Valley, WA.
|
We have found that the answers are close but not exact. That is because every vendor models the protective devices differently. Also, the conductor libraries are often not exactly the same. Slight differences in impedances will cause slight differences in short circuit currents, and arc flash energies.
The only time I have seen a huge deviation was after a Vendor updated their software and the new version did not calculate line to ground faults correctly.
_________________ Robert Fuhr, P.E.; P.Eng. PowerStudies
|
|