| Author: | AB P.E. [ Thu Oct 14, 2010 5:53 am ] |
| Post subject: | Oct 12 Arc flash fatality per MSHA |
Preliminary report at this link: http://www.msha.gov/FATALS/2010/2010MNM16prelim.pdf Preliminary report says 3 workers were installing ground fault indicator lights on 800 Amp breaker. Arc flash occurred, 3 injured, 1 died 2 days later. MSHA follows with more details in a "Fatalgram" usually in 2 or 3 weeks. The final report will be issued after a much longer time. |
|
| Author: | AB P.E. [ Fri Nov 05, 2010 5:59 am ] |
| Post subject: | |
Fatalgram now on MSHA site. The "Fatalgram" for the accident is now on the MSHA site. http://www.msha.gov/fatals/2010/FAB10m16.asp Remark, the Fatalgram indicates the breaker was bottom fed. Never my first choice for breaker feed. Also notice there is an opportunity to submit suggestions. |
|
| Author: | AB P.E. [ Wed Jan 12, 2011 2:09 pm ] |
| Post subject: | |
MSHA Report of Investigation The MSHA report is now available. http://www.msha.gov/FATALS/2010/FTL10m16.asp Worth scrutiny. |
|
| Author: | glen1971 [ Thu Jan 13, 2011 6:23 am ] |
| Post subject: | |
After a quick glimpse of the report, it looks as though they assumed the Utility Supply was on the top of the breaker. Using a meter to check for voltages prior to starting their job would have saved his life... NEVER assume anything!! People forget that you can't see electrical, like you can with steam, water, etc... It WILL bite you if you are complacent and cut corners... |
|
| Author: | Robertefuhr [ Sat Jan 15, 2011 9:40 am ] |
| Post subject: | |
The report clearly indicates the importance of testing for voltage using "Live-Dead-Live" procedure. Always verify line and load side terminals. |
|