1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Clearing Time Upstream of Transformer

Discussion in 'System Modeling and Calculations' started by deprico, Mar 25, 2008.

  1. deprico Member

    Hello,

    I am performing and arc flash analysis and have run into a problem figuring out what clearing time to use. I am given the bolted fault current at the transformer secondary and the transformer specifications. The 150Kva transformer has secondary of 208V and a fault current of 32000 A. I have been told there are 100 K fuses upstream of the transformer along with some time delay breakers.

    How do I figure out what clearing time to use for an arc at the transformer secondary? The upstream breaker has a delay of 2.5 and the fuse clearing time varies wildly based on the current.
  2. acobb Well-Known Member

    deprico,

    First of all it appears that the utility gave you the "infinite source" value of fault current. 150 kVA, 208v, and 32000 amps, indicates no source Z other than a 1.3% impedance transformer. I would go back to them and ask for the actual fault duty at the secondary terminals with the MVA base and sequence values. I think your actual values will be much less.

    You will also need specifics about the utility protective devices so that you can get the appropriate time current curves to use in your analysis.

    Alan
  3. haze10 Well-Known Member

    Is this a utility supplied transformer. If so, there upstream overcurrent protection could be set quite high and be quite slow. IE levels could be quite high on the secondary. However, the secondaries normally go into the customers main panel that has a main circuit breakers. Is this true for you. If yes, then why would you need to work on the transformer or cables upstream of your MCB. For clearing time you would use your MCB.
  4. deprico Member

    Well say I am doing live work in the panel that houses the main breaker. There still exists an exposure to the secondary on the line side of the breaker inside the panel. This would mean the clearing time of the breaker does not come into play for a fault on the line side of the breaker. For this I would need the clearing time for the protective device upstream of the breaker.
  5. Gary B Well-Known Member

    It is not unusual, for the situation you describe, for the arc flash exposure to be unworkable.

    The transformer primary fuses will provide some protection that may be calculated through the transformer but typically that is too slow to provide arc flash mitigation.

    It is a common problem on the sites we've looked at, only official solution is to take an outage.
  6. haze10 Well-Known Member

    Safeguard the line side with a rubber blanket or suitable shield, and stay out of the Prohibited Approach Boundary - 1" on a 480V. Then you are only concerned with the load side. If you have to work on the line side, then you have to de-energize.
  7. mnmurphy New Member

    how to calculate.

    Generally, what I do when the upstream device is on the high side of the transformer is use the 2 seconds. If I am labeling the transformer I do this because I am not aware of any testing on arc flash events on the transformer (and how it responds to an arc), and also because the upstream device is often set high (or up on a pole and hard to get).

    However, you can do this... If you "arc" the bus where the arc flash is, you want to see what the current is flowing through the upstream device on the high side of the transformer. This current is obviously at a different voltage, but so is the protective device upstream. Most programs should be doing the calculations this way - you might just check with them.

    If you are using the IEEE Spreadsheet, this is pretty difficult to do. Given the impedance of the transformer it is a pretty safe bet that a low voltage arc on the low-side may not trigger a trip on the high side very quickly. Use 2 seconds and the 32000 Amps they gave you.
  8. haze10 Well-Known Member

    Don't you think to some extent we are over analyzing this. Are you seriously going to take the whole panel to Level 4 because of the line side lugs on the main, when the electricians are working on the load side which could be Level 2. Remember that only 'Qualified' individuals can do this work. I think that training includes knowing that the line side mains are different than the load side. Just me but I think we have to enter some degree of practicality and reasonableness.
  9. WDeanN Well-Known Member

    haze,
    The problem is that in an unsegregated bus, the flashover could carry over to the line side terminals of the main breaker. In this case, the main is useless. If the bus has a separate compartment for the main breaker, then what you say is true, and that is the way that I calculate it. I put two stickers on equipment with segregated main breakers. One on the Main, and one on the rest of the bus. But panelboards get just one sticker, calculated ahead of the main breaker.
  10. wbd Well-Known Member

    Typically for equipment except for switchgear where the compartments are very segregated, you have exclude the main incoming panel breaker for arc flash hazard analysis. The reasoning is that the main lugs on the incoming breaker or fuse are most likely exposed and any fault inside that panel would cascade rapidly to encompass these lugs. The fault then has to clear from the next upstream breaker or fuse, which is most likely on the high side of the transformer.
  11. haze10 Well-Known Member

    On a 400 to 800A MCB panel, the top of the load bus is probably 12" or more to the line lugs on the MCB. So you would be outside the Restricted approach. So we are saying that a load side flash will ionize the air to the point the line lugs are now flashing over. Seems somewhat unlikely to me. I would still think that a cover over the line lugs is all that is needed. I would not be surprised to see the next Square D upgrade to be a bolt on plastic cover over the line lugs.