1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Verifying "Dangerous" Category is Deenergized

Discussion in 'Electrical Safety Practices' started by tmc7, Feb 25, 2010.

  1. tmc7 New Member

    When verifying that a conductor or circuit has been deenergized, the appropriate PPE must be worn to verify nominal voltage. How do others verify zero voltage on 40+cal panels when there is no PPE rated to protect the person?
  2. Zog Well-Known Member

    I have never seen a good answer for that one, every plant has the same question. Use distance as your friend by suiting up and using hot stick mounted meters or phasing sticks and shotguns for applying your grounds if required.

    The best solution is mitigating the hazard level to <40cal/cm2.
  3. Canuck01 Member

    Zog, I agree 100%
    Some of my questions are:
    Does the test need to be "touch" or is an inductive tester sufficient?
    Should an Arc Flash label contain more than 1 working distance (like a testing distance) since there are places where the +40 cal IE might even extend beyond the reasonable access distance for the equipment.
  4. wbd Well-Known Member

    I guess there are several items to check:
    1. In the AFH study, was a 2 sec cutoff used if you able to taking into account physical configuration?
    2. Is it possible to lower the AFH by lowering the Inst setting on a feeder breaker if there is one?
    3. Is this HRC of 4, for a working distance of 18"? What happens if the working distance is greater?
    4. If contact testing is required, can long leads from a meter be attached to appropriate length hotsticks?
    5. If proximity probe is acceptable, can that be attached to an appropriate hotstick?
    6. Is it possible to use voltage meter installed on bus (if there is one)?
  5. Vincent B. Well-Known Member

    If you see it at 0 V, does it indicate that there's no voltage on the bus or is it just malfunctioning or wrongly wired? Is voltage absent from all 3 phases (3x line-line and 3x line-ground) or is there a remaining live phase?

    Permanently attached meters do have pitfalls.
  6. Zog Well-Known Member

    A panel mounted meter does not meet the requirements of 120.1(5) of the 70E.
  7. Canuck01 Member

    Testing after de-energising

    Is the test required to be contact or is a proximity test sufficient?

    CSA Z462-098 Clause 4.2.1(e) or NFPA 70E 2004 120.1(5)
    "Use an adequately rated voltage detector to test each phase conductor or circuit part to verify that
    they are de-energized. Test each phase conductor or circuit part both phase-to-phase and
    phase-to-ground. Before and after each test, determine that the voltage detector is operating
    satisfactorily." Note: See CAN/CSA-C22.2 No. 61010-1 for rating and design requirements for voltage measurement and test
    instruments intended for use on electrical systems operating at 1000 V and below.


    I say contact testing under 1000 volts. Non-contact testing could be implied above the 1000 volt threshold.

    Still, the question remains - how to verify absense of voltage when above 40 cal @ calculated working distance...
    My thoughts:
    Confirm the IE is accurate. Some studies are flawed (2 second rule, etc)
    Run scenarios using different working distances. Find a distance with less than 40 cal. This still leaves the question of multiple labels on switchgear...
  8. jghrist Well-Known Member

    Could de-energizing (and verifying) upstream be acceptable if there is no other source of power and if the upstream location has a lower IE and can be de-energized? In particular, I'm thinking about the primary of a transformer where the high IE on the secondary is caused by slow primary overcurrent protection.
  9. Canuck01 Member

    I like the idea of it, however upstream testing is really only good for an uncomplicated branch on the electrical system. Some installations (including mine) have multiple MCCs fed from the same transformer so it's not feasible to test upstream.
  10. Canuck01 Member

    Webcast

    https://event.on24.com/eventRegistration/EventLobbyServlet?target=registration.jsp&eventid=197971&sessionid=1&key=CFEF79712F935A639C8FE0BD379D4E3B&sourcepage=register[/URL]

    A free webcast from Fluke for those who are interested...
  11. minni-mo New Member

    check two items feed down stream with lower hrc frist then verify the the dangerous
  12. jghrist Well-Known Member