1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Main SG analysis ok or total needed ?

Discussion in 'Electrical Safety Practices' started by PUCKMAN, Feb 21, 2010.

  1. PUCKMAN Member

    1. Our mcc's have some sq. d mph or mpl cb's 800amps @ 50ka with adjustable instan. They are used as tie breakers and main cb in mcc.

    2. Our main 4000amp switchgear station and mostly 600amp breakers are rated @100ka and 85ka .

    After along discussion with safety about labeling and a analysis they sort of agreed on analysis on the main swichgear only. [ #2 ]

    Where does that leave the mcc panels as far as using the tables ?

    They want to use osha where they can and say to use the 70e tables for the tasks . I explained about being in the parameters for using 70e.

    Would'nt the size of mcc cb's [ #1] require a analysis also? Do not know the clearing time of them either.
  2. Zog Well-Known Member

    I think I follow you, your plant decided not to do the study on the MCC's and use the tables instead right?

    The 800A breakers are the mains feeding the MCC's?

    They based this assumption, that they can use the tables on the AIC rating of the breakers?

    Do the 800A breakers feeding the MCC's have an INST trip?
  3. PUCKMAN Member

    The 800amp 50KA cb in mcc have a instantanous setting low to high. And they said they will get a analysis on the main SG. We'll see.
  4. Zog Well-Known Member

    If they have an INST trip and are properly being applied within the 50kA rating, the tables should be able to be used. But the term low to high for INST settings is throwing me off. Usually they are multpliers like 10x, 12x, etc...