1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Incident Energy andCL Fuse Equations

Discussion in 'System Modeling and Calculations' started by SJB, Feb 1, 2010.

  1. SJB New Member

    Does anyone else have a problem with the IEEE 1584 incident energy equations for current limiting fuses?

    Incident energy is based on the arcing fault current, not the bolted fault current. Arcing fault current is determined from the bolted fault calculation but takes several other variables into consideration, like system voltage, gap, etc. The CL fuse incident energy equations only use bolted fault values.

    Why are the CL fuse equations based on bolted fault rather than arcing fault values?

    For now, I am not using the equations in my analysis. Are my concerns unfounded?

    Thanks.
  2. Zog Well-Known Member


    Current limiting fuses are only effective at reducing Ei when operating in the current limiting range, something the fuse manufacturers don't like to talk about.
  3. acobb Well-Known Member

    But the protection guys must know!
  4. Zog Well-Known Member

    Know how to best sell fuses that is.
  5. brainfiller Administrator

    During the development of IEEE 1584, had only a handful of tests with current limiting fuses. CL fuses have a different response depending on how much short circuit current is flowing and whether the current is in the CL range or the non CL range.

    It is easier just to measure the incident energy and create an equation rather than try to predict the arcing current which is based on the fuse operating in its current limiting mode.

    You can still have a high incident energy while using CL fuses if they respond too slow. If the short circuit current is too low, the fuse can take time to respond similar to breakers and other devices. The CL fuse must be properly sized.