1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Higher IE on CB Load Side

Discussion in 'General Discussion' started by viper57, Jan 15, 2010.

  1. viper57 Member

    Looking at an arc flash study done on a 13.8kV SWGR line up with main breaker. The detailed study shows a significantly higher IE (44.8 cal/cm2) on the load side of some of the breakers than on the SWGR bus (22.8 cal/cm2). These breakers are feeding large motors (5000+HP). Just doesn't seem right.:confused: What, if anything, might cause this?
  2. Zog Well-Known Member

    Motor contribution is my guess, hard to tell without all the data. Possiblle you can adjust relay settings to lower this. Sounds like a good canidate for remote racking and switching.
  3. viper57 Member

    How could motor contribution affect the load side and not the line side of the breaker? Could you send me a PM on your company and services offered? Thanks!
  4. WDeanN Well-Known Member

    It's also possible that there is some additional protection on the bus that does not protect the load side equipment, such as differential protection or zone selective interlocking. They may also be taking credit for maintenance settings on the relays at the bus, but not at the motors.

    The numbers still seem high on the bus side for this, however. I would look at the study and see if they looked to upstream devices for miscoordination or faster operating times at the arcing fault current levels.
  5. THE CABLE GUY Well-Known Member

    Can you post a segment of your one-line that indicates what your speaking of? Sorry, I am a visual type of guy.