1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

GE 750 -ve seq

Discussion in 'General Discussion' started by amohammed, Jan 5, 2010.

  1. amohammed New Member

    Has anyone setup a GE 750 relay to provide protection against unbalanced faults using the negative sequence element? I have been told the recommended setting for the relay would be 50% of Phase TOC pickup with other settings remaining the same. Is this a good assumption?
  2. short-circuit52 New Member

    I would run a unbalance fault analysis on the circuit in question first. Unbalanced fault current is tough to determine and relies on zero sequence component values in cables, buses, etc. as well as the fault return path impedances. 50% sounds more like a factory setting to me.
  3. amohammed New Member

    I found this paper in IEEE's database that explains how to coordinate the negative sequence elements. Its called Negative Sequence Overcurrent Element Application and Coordination in Distribution Protection written by Elneweihi, Schweitzer and Feltis.
    Per the paper, |3I2/Ip| = Sqrt(3). I can figure out the pickup based on this equation and other coordination requirements described in the paper.