MCC -Deenergized

Discussion in 'Electrical Safety Practices' started by Brodie, Dec 4, 2009.

  1. Brodie Junior Level

    On Board

    TX-I used to agree with the same practice you follow,pro maintenance,least disruptive to operations.

    A close call with a Motor Starter Blowing up,an underated Circuit Breaker 35 ka in a 65 ka assembly,250 amp breaker set @ inst trip of 2500 amps,all due to poor insulation on a motor junction box .

    The probability of this happening again is high until all associated motor connections are inspected and inst.trip settings adjusted as well as the AIC rating increased on the buckets.

    These particular buckets are Siemens mfg. with a lot of open grill work in the front panel,a lot like a barbecue grill!You know most disasters are a combination of events,In this case I realized the contained explosion could have migrated to a full blown MCC meltdown,due to a combination of design factors.

    In the end,companies can say the employee was not following the rules.I guess one really needs to study the design of the system and weigh the risk against the likelihood,I now feel as though deenergized is the way to go.It may be a pain but so is having your skin peeled off in a burn center!

    Is it really worth the risk? How long has this been going on? Maybe too long..be safe..Thanks for the response
  2. Brodie Junior Level

    Statistics

    I have heard that 40% off all Arc Flash incidents are due to equipment malfunction,In other words no one working on the equipment.Does anyone have information on these percentages?
  3. TxEngr Sparks Level

    Brodie,

    I completely agree with your comment that you must analyze the equipment and installation you have and make the best/safest decisions you can based on that information. My comments are based on the minimum requirements as I read them in the various codes. That becomes your starting point for making safe decisions.

    When dealing with older equipment, the minimum is often not enough. That's why I'm in the process of a 3 year upgrade of some of my low voltage switchgear. At other places I've worked, the MCCs couldn't even be locked out properly. They were so old, they didn't even have locking mechanisms on the starter doors and we had to modify the starters to add locking mechanisms. It just points out that you must take the age and condition of the equipment into mind when establishing safe procedures.

    Good luck and stay safe.

    TxEngr
  4. haze10 Sparks Level

    My comments related to the breaker being designed to an acceptable AIC rating. As stated, it did not refer to Arc Fault IE. You do not need to 'derate' to 80% the manufacturers AIC. If you read the UL method for determining the AIC you will see that it is done at an extremely low power factor which would result in very high peak asymmetrical amps. The power factor in most applications will be much higher with lower peaks. There are enough safeguards built into manufacturers rating already, you don't need to add more.
  5. acobb Sparks Level

    Haze,

    I assume your 80% post is in regard to my previous since there have been no others about the issue, if not please disregard. Distribution systems are dynamic and that is why I opt for the margin. I make a living working on these systems, and have for the past 30 years, so I know the variances. Otherwise, do you really want to expect a 20 to 40 year old piece of equipment to have to do the max. I don't.

    I have seen cabinets and 3" steel angle legs buckled on old oil filled breakers that were not exposed to faults in excess of their initial rating, and much less than my 80% max.

    I know that it is arbitrary, but we do need to do some due diligence.

    If your employer stresses you to the max at every crucial point, I expect you will end up needing some margin as well.
  6. Flash Junior Level

    Another engineers view:

    1. There is no such thing as a secondary calculation on the bucket. The fault can propagate to the line side of the bucket and even to the line side of the incoming main device. I have pictures of two such incidents, one was a death. Secondly, the lower fault current can increase the IE.

    2. In addition, an MCC is a prime example of a barrier or horizontal case, this increases the the IE beyond the typical 1584 calculation. Refer to Mike Lang's paper on the Ferraz website for clarification.
  7. Brodie Junior Level

    Pictures

    Fash I would like to view your photos,I would like to make others aware of the possibilities and consequences of arc flash migration.In my personal case an overdutied breaker in the MCC bucket AIC 32 in a 65 KA MCC could have led to such an incident.
    The facility I work in has several of these breakers.The Short Circuit Study only reccomended replacement,In my opinion these breakers must be replaced and until they are unsafe work conditions exist within the plant:mad: