1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

Arc Flash Boundary above 600V

Discussion in 'General Discussion' started by haze10, Feb 8, 2008.

  1. haze10 Well-Known Member

    I find this a little confusing and could use some guidance. Lets say we are using the analysis method. We need to calculate the Arc Flash Boundary. We have the choice of the Ralph Lee equation or the IEEE 1584 equations presented in the Annex D.

    Now, my opinion is that since the Ralph Lee formula is part of the original code, it must take preference over anything in the Annex. The problem is that code stipulates that the Ralph Lee formula is only good up to 600V.

    The IEEE equations in Annex D, I assume by the introduction, are good up to 15KV. But there is a variable, that changes value, whether it is under 1KV or over 1KV.

    So would this mean we use the Ralph Lee formula up to 600V, and then switch to the IEEE formula to 1KV, and change again above 1KV.

    I know you could use the IEEE formula at any value below 1KV but it seems contrary to substiture an Annex formula in lieu of the code supplied formula.

    Am I over complicating this or did I miss some fundamental point?
  2. WDeanN Well-Known Member

    In general, most people use the IEEE formulas up to 15kV, and then revert to either the Ralph Lee equations, or another model like the Duke Energy calculator, or ArcPro.

    As to you complicating the matter, I don't think so. See http://www.arcflashforum.com/showthread.php?t=50