1. Create Your User Profile and Status Updates

    Arc Flash Forum members are invited to create a user profile. Let others know who you are, what you do and even add a picture or avatar of yourself. What are you up to? Let people in the arc flash and electrical safety community know with "status updates"!
  2. Welcome to the All New Arc Flash Forum

    Arc Flash Forum is a community where we help each other learn about arc flash and electrical safety. There is still much to be learned about arc flash, standards, PPE, studies and more and We need your HELP!

    If you have good information about Arc Flash - Post It! If you have a question about Arc Flash - Post It! If you can provide answers to Arc Flash questions - Post it!

    Sign up as a today member! Feel free to link to this site www.arcflashforum.com. Tell your friends. We want to help everyone be safe in the workplace!
  3. Bigger and Better!

    As you have no doubt noticed, the forum has been through quite an upgraded and looks and feels very nice! There are loads of new features and ways in which this site can now be even more useful to the community in learning about Arc Flash and Electrical Safety.

    Create your detailed user profile
    Add a profile photo of yourself
    Like the forum on Facebook
    "Like" users' posts
    Publish your articles in the library
    ...and much, much more!

    Learn More About the New Features Here

What To Label Panel?

Discussion in 'Arc Flash Labels' started by PAult, Nov 5, 2009.

  1. PAult Member

    See the attached pic.

    What PPE CAT and IE level should I label the 208/120 Panel?

    Thanks

    Attached Files:

  2. Zog Well-Known Member

    Well, what the study says, HRC 3. However, I would question these results, do you know all the info used for the calulation?
  3. THE CABLE GUY Well-Known Member

    This is what my label would look like. This would be for three phase not single phase.
    My calculations does not include your upstream utility data.:)

    Attached Files:

  4. PAult Member

    See the attached for more detail, using IEEE 1584 study in SKM. Basically at the max clearing time of 2.0 Seconds.

    Since this Xfmr is <125 KVA and it is 208V would you label it any different?

    Thanks

    Attached Files:

  5. PAult Member

    I like the label.. Looks like this is generated from easypower? Do you do a study on all your transformers <125KVA? why 2* rather than 3? Did easy power calc this?

    Thanks
  6. PAult Member

    With all the <=125KVA transformer and 208VAC arc substaining issues I think I will just use the 70E table for this application and label it with HRC 1 and an 4ft AFB.

    What does everyone think?

    Thanks
  7. WDeanN Well-Known Member

    Well, I'm one who HATES using the Hazard/Risk Categories and 70E tables.

    I haven't had to do this yet, so who knows what the final product would be, but since the transformer is only 75kVA, I would avoid putting a calorie rating on the label if I could, but would include a minimum PPE as all natural fiber, long sleeve shirt and pants, hard hat, face shield, and gloves.
  8. jghrist Well-Known Member

    Exception No. 1 to 130.3 indicates that an arc flash hazard analysis is not required for 208V panels served by single transformers less than 125 kVA. IEEE Std 1584 states that

    "The arc-flash hazard need only be considered for large 208 V systems: systems fed by transformers smaller than 125 kVA should not be a concern."

    The clear implication is that an arc flash hazard does not exist and that because the arc will not self-sustain, the IE will be less than 1.2 cal/cm². I believe that labelling to require Category 0 PPE, 1.2 cal/cm² PPE, or even not labelling would be acceptable to meet NFPE 70E requirements. The NFPE 70E handbook for 130.3(C) states that

    "Only the equipment where the incident energy level is greater than 1.2 cal/cm² needs to be marked, but that decision depends on a facility's safety program."
  9. PAult Member

    I thought everything that may require service while live needed to be labeled?? I cannot find anything in 70E where it says only greater than 1.2 cal/cm2 needs to be labeled, what section is this in?

    Thanks
  10. jghrist Well-Known Member

    Before that quote, I wrote
    This is in the handbook and not in the NFPA 70E text, so it is not governing, but the requirements for arc flash hazard labelling are all for locations where there is a potential arc flash hazard as defined in Article 100.
  11. THE CABLE GUY Well-Known Member

    I would suggest a label at least to include HRC0 because you do not want to forget about the shock hazard and associated hazard boundaries.

    I also recommend that the "Fed from" information is posted on the label to let the customer or worker easily ID the upstream protective device.
  12. PAult Member


    Since the NEC 110.16 requires some kind of label on the equipment we are going to put the PPE category and the minimum required PPE on the labels. If we didn't label this panels with the required PPE wouldn't we have to use the tables to determine it?
  13. THE CABLE GUY Well-Known Member

    Hello PAult,
    I hope we are not confusing you.
    I would just set your own method and not worry about the tables.

    Basically, you need a company standing statement, training and noted in your final report of how to handle the HRC for task when working on this type panelboard and referencing the NFPA 70E exception to 208vac,<125KVA.

    IMO, you can make this a HRC1, HRC2 or HRC3. Just make the decision and stick with it for all situations with such criteria. It’s the best thing you can do until something more definitive is determined.
  14. PAult Member

    Thats what I will do.

    Thanks for the Help!!
  15. Terawatt New Member

    This looks like SKM
  16. Terawatt New Member

    Low Arc Flash Hazards

    The attached file is what I use for all panels/enclosures fed by single source transformers < 125kVA, V<=240. We label for uniformity and clarity.